Search found 26 matches

by om_tech_support_AC
Wed Jun 20, 2018 7:13 am
Forum: Stepper Motors and Controls
Topic: Stepper Motor with Positioning Feedback Signal (like servo motor)
Replies: 3
Views: 76

Re: Stepper Motor with Positioning Feedback Signal (like servo motor)

The CVK series is an open loop system so there is no feedback to the driver. We do offer PKP motors with encoders but the feedback would have to go to a controller. For the controller we offer the SCX11 (linked below) which has an input for an external encoder. https://catalog.orientalmotor.com/item...
by om_tech_support_AC
Wed Jun 20, 2018 7:06 am
Forum: Stepper Motors and Controls
Topic: Looking for a user manual for D2D2043-s
Replies: 1
Views: 27

Re: Looking for a user manual for D2D2043-s

Hi jhchopper,

Below is the manual for D2D2043-S.

D2D2043-S.pdf
(99.53 KiB) Downloaded 3 times
by om_tech_support_AC
Tue Jun 19, 2018 7:12 am
Forum: Stepper Motors and Controls
Topic: Stepper Motor with Positioning Feedback Signal (like servo motor)
Replies: 3
Views: 76

Re: Stepper Motor with Positioning Feedback Signal (like servo motor)

Hi Essenceindia, For stepper motor and drivers that offer a feedback signal both the AR and AZ series have the ASG/BSG as a feedback output. For the AR series the pulse input type driver offers the resolver feedback via ASG/BSG. For more information about the AR series ASG/BSG output please refer to...
by om_tech_support_AC
Tue Jun 19, 2018 6:54 am
Forum: Speed Control Systems
Topic: BMU & BLH Series Clarificatons
Replies: 3
Views: 416

Re: BMU & BLH Series Clarificatons

Hi Essenceindia,

For the BMU series there are I/O that can be controlled via a PLC. For information about wiring the I/O please refer to the link below.

http://www.orientalmotor.com/products/p ... df#page=16
by om_tech_support_AC
Tue Jun 12, 2018 6:41 am
Forum: AC Motors
Topic: Oriental AC Motors with VFD Combination Suitablity
Replies: 3
Views: 248

Re: Oriental AC Motors with VFD Combination Suitablity

Hi Bryant,

Oriental Motor only offers Fuji inverters. If you would like a Third-party inverter can be used with our three phase induction motors.
by om_tech_support_AC
Mon Jun 11, 2018 9:15 am
Forum: Speed Control Systems
Topic: Suitable BLDC Motor
Replies: 1
Views: 80

Re: Suitable BLDC Motor

Hi essenceindia, The recommended 200 W Brushless DC motor with a speed range of 0.2 to 10 rpm would be BXS6200A-200S. Depending upon your PLC the BXS6200A-200S can have the speed controlled via external DC voltage (0-10 VDC), external potentiometer or 16 digital operations. The 16 digital operations...
by om_tech_support_AC
Mon Jun 11, 2018 9:01 am
Forum: AC Motors
Topic: Power factor for 15W AC induction motor
Replies: 2
Views: 71

Re: Power factor for 15W AC induction motor

Hi DonC, For 3IK15A-SW2 the power factor is 0.52. The input power is calculated by multiplying the voltage 220 VAC by current 0.15 A resulting in 33 W. The voltage and current specs for 3IK15A-SW2 can be found using the link below. https://catalog.orientalmotor.com/item/all-categories/15w-world-k-se...
by om_tech_support_AC
Mon Jun 04, 2018 7:07 am
Forum: Linear and Rotary Actuators and Controls
Topic: Communicate with an AZD-KD step driver using a laptop
Replies: 1
Views: 92

Re: Communicate with an AZD-KD step driver using a laptop

Hi Jcacace, For the USB to RS485 converter it would be suggested to use the MWE820A. For more information about MWE820A and the pinouts please refer to the document below. http://www.orientalmotor.com/products/pdfs/RS485-Converter-(USB)-v2-0.pdf It is possible to control up to 31 slaves using a mast...
by om_tech_support_AC
Fri Jun 01, 2018 11:37 am
Forum: AC Motors
Topic: KII Series AC Geared Motors Overheating
Replies: 6
Views: 200

Re: KII Series AC Geared Motors Overheating

For the K2 Series motors they will overheat at 100 C case temperature so if they are not tripping the thermal protector they are within specification. There isn't much else we can do via the forum but you could contact your local sales office below for further help. ORIENTAL MOTOR (INDIA) PVT.LTD. N...
by om_tech_support_AC
Thu May 31, 2018 7:09 am
Forum: AC Motors
Topic: KII Series AC Geared Motors Overheating
Replies: 6
Views: 200

Re: KII Series AC Geared Motors Overheating

5IK90GCT2-36 or 5IK90GCT2-7.5 are meant for single phase 220/230 VAC 50 Hz. By operating at 60 Hz it is causing the higher temperature in the motor. The recommended motors for single phase 220/230 VAC 60 Hz is 5IK90UCT2-36 and 5IK90UCT2-7.5. The motor surface temperature may exceed 70 °C (158 °F) ev...
by om_tech_support_AC
Wed May 30, 2018 7:49 am
Forum: AC Motors
Topic: KII Series AC Geared Motors Overheating
Replies: 6
Views: 200

Re: KII Series AC Geared Motors Overheating

Hi Essenceindia,

What is the frequency of the single phase 220/230 VAC? Do the 5IK90GCT2-36 or 5IK90GCT2-7.5 stop operating when they overheat? What is the ambient temperature?
by om_tech_support_AC
Wed May 30, 2018 7:44 am
Forum: Stepper Motors and Controls
Topic: why stepper motor doesn't move?
Replies: 2
Views: 103

Re: why stepper motor doesn't move?

Hi Fikadu, The input voltage specification for the CW input and CCW input is 5 VDC. If the voltage exceeding 5 VDC is applied, connect an external resistor R1 so that the input current becomes 7 to 20 mA. Since you are using 15 VDC you'll need the external resistor to limit the current. For more inf...
by om_tech_support_AC
Thu May 17, 2018 7:05 am
Forum: Stepper Motors and Controls
Topic: ARD-KD: resetting overvoltage alarm through rs-485/modbus-rtu
Replies: 3
Views: 147

Re: ARD-KD: resetting overvoltage alarm through rs-485/modbus-rtu

Changing NET-IN7 to alarm reset would be a type C timing update. Therefore you would have to write to the non-volatile memory even during start up and would require the cycle of power or executing the configuration command register 397 decimal or 018Dh.

Timing update.JPG
Timing update.JPG (27.64 KiB) Viewed 129 times
by om_tech_support_AC
Wed May 16, 2018 12:14 pm
Forum: Stepper Motors and Controls
Topic: Stepper Motor Detent Torque
Replies: 0
Views: 79

Stepper Motor Detent Torque

Q: My application is an indexing conveyor with an incline at 10 degrees. I would like to use a geared stepper motor for this application, but if power is lost, I want to ensure there is enough resistance to hold the position. A: The resistance in a non-excited stepper motor is known as detent torque...
by om_tech_support_AC
Tue May 15, 2018 8:48 am
Forum: Stepper Motors and Controls
Topic: ARD-KD: resetting overvoltage alarm through rs-485/modbus-rtu
Replies: 3
Views: 147

Re: ARD-KD: resetting overvoltage alarm through rs-485/modbus-rtu

Hi Vazkus, For the RS-485/Modbus input or NET-IN the alarm reset is not one of the 16 NET-IN for factory default. To change the NET-IN you will have to write 24: ALM-RST to one of the registers listed in the table below. NET-In.JPG For example you could write 24 Decimal to register 2231 to change NE...
by om_tech_support_AC
Mon Apr 16, 2018 1:38 pm
Forum: AC Motors
Topic: Oriental AC Motors with VFD Combination Suitablity
Replies: 3
Views: 248

Re: Oriental AC Motors with VFD Combination Suitablity

Hi Shree, All the three phase induction motors on the website are VFD rated. You can use them with a third-party VFD or we can recommend a Fuji Inverter based on the motors power (W or HP) and input voltage VAC. For the single phase 220~230 VAC induction motors those are not VFD rated. However we of...
by om_tech_support_AC
Thu Apr 05, 2018 11:46 am
Forum: Thermal Management
Topic: What happen when inlet airflow of an AC vacuum motor is blocked
Replies: 3
Views: 437

Re: What happen when inlet airflow of an AC vacuum motor is blocked

Since it is not an Oriental Motor product I cannot determine what factors are causing the fan to heat up faster then the winding. Also even if it was our product the AC induction motors we offer are not vacuum rated.
by om_tech_support_AC
Tue Apr 03, 2018 7:37 am
Forum: Thermal Management
Topic: What happen when inlet airflow of an AC vacuum motor is blocked
Replies: 3
Views: 437

Re: What happen when inlet airflow of an AC vacuum motor is blocked

Hi Qwe,

What is the part number of the motor you are using? How are you measuring the temperature of the windings?
by om_tech_support_AC
Tue Apr 03, 2018 7:25 am
Forum: Speed Control Systems
Topic: DSC Speed Control Motor Installation
Replies: 3
Views: 448

Re: DSC Speed Control Motor Installation

Unfortunately the only wiring diagram we offer for DSCI590EC-75-3 and DSCI560UA-A-3 can be found on pages 15, 16 and 17 in the linked manual below.

http://www.orientalmotor.com/products/p ... df#page=15
by om_tech_support_AC
Mon Apr 02, 2018 9:58 am
Forum: Speed Control Systems
Topic: DSC Speed Control Motor Installation
Replies: 3
Views: 448

Re: DSC Speed Control Motor Installation

Hi Essenceindia, What is the part number of the DSC series that you are using? What part of the wiring are you having trouble with: the power supply, I/O or capacitor? Have you referred to page 15, 16 and 17 in the linked manual below? http://www.orientalmotor.com/products/pdfs/opmanuals/HM-9345-2E....
by om_tech_support_AC
Thu Mar 29, 2018 1:33 pm
Forum: Stepper Motors and Controls
Topic: AR Series Flex Sequencial Positioning
Replies: 1
Views: 373

Re: AR Series Flex Sequencial Positioning

Hi Rodolfo,

Unfortunately the AR Series does not have the ability to run an infinite loop without re-triggering an input after the 4 linked motions are complete.
by om_tech_support_AC
Fri Mar 23, 2018 7:42 am
Forum: AC Motors
Topic: Tension control with a torque motor for winding applications
Replies: 1
Views: 367

Re: Tension control with a torque motor for winding applications

Hi vroomeng,

Unfortunately we do not have a formulaic version of the torque-speed chart. The chart is a reference the actually torque and speed will vary from the given values so it would be best to test different voltages to find your desired torque for the given tension, and winding speed.
by om_tech_support_AC
Wed Jan 31, 2018 12:30 pm
Forum: Speed Control Systems
Topic: Fuji 1/8 HP inverter with 15 W induction motor
Replies: 0
Views: 552

Fuji 1/8 HP inverter with 15 W induction motor

Q: What parameters do I need to set on the FRN0001C2S-6U inverter to use with the 15 W 3IK15A-SW2/ 3IK15GN-SW2 motor? A: Since the FRN0001C2S-6U* inverter is rated for 1/8 HP (90 W) motors, to prevent the overheating of the 1/50 HP (15 W) 3IK15GN-SW2 motor the following parameters need to be changed...
by om_tech_support_AC
Wed Sep 06, 2017 12:23 pm
Forum: Stepper Motors and Controls
Topic: AZ pulse input wiring to SCX11
Replies: 0
Views: 670

AZ pulse input wiring to SCX11

Q: Is there a wiring diagram for SCX11 to AZ pulse input type in the SCX11 manual? A: Since the AZ was released after the SCX11 there is not a wiring diagram similar to the SCX11 to AR found in the operating manual. However, below is a pin for pin connection and also a sink/source connection. The SC...