Hi,

Sometimes when setting overly high speed or/and low acceleration I get the 'overvoltage' alarm/warning. I understand what that means, I show proper warning message to the user with recomendation to reduce the speed and increase the acceleration. The problem is I am unable to reset this alarm through modbus-rtu. I can do that through MEXE software, but that is not acceptable in my user setup...
How do I do it through modbus?

Thank you.

om_tech_support_AC
Posts: 26
Joined: Tue Jan 03, 2017 2:53 pm

Re: ARD-KD: resetting overvoltage alarm through rs-485/modbus-rtu

Postby om_tech_support_AC » Tue May 15, 2018 8:48 am

Hi Vazkus,

For the RS-485/Modbus input or NET-IN the alarm reset is not one of the 16 NET-IN for factory default. To change the NET-IN you will have to write 24: ALM-RST to one of the registers listed in the table below.

NET-In.JPG
NET-In.JPG (52.65 KiB) Viewed 137 times


For example you could write 24 Decimal to register 2231 to change NET-IN7 from no function to an alarm reset. Once the NET-IN is change it must be saved to the non-volatile memory. The non-volatile memory is register 403 decimal or 0193h and writing a 1 to that register will save the changes to the NET-IN. After saving to the non-volatile memory cycle the power on the driver. For more information about non-volatile memory please refer to the link below.

http://www.orientalmotor.com/products/p ... f#page=230

Now you can write to the driver input command address 007Dh. For the example we changed NET-IN7 to alarm reset so we would write 80h or 128 decimal.

Command inputs.JPG
Command inputs.JPG (31.96 KiB) Viewed 137 times


Another option would write a 1 to register 385 Decimal or 0181h to reset the alarm. If another alarm occurred then a 0 followed by a 1 would be required to turn off the alarm reset and then turn it back on again.

vazkus
Posts: 6
Joined: Fri May 11, 2018 2:30 pm

Re: ARD-KD: resetting overvoltage alarm through rs-485/modbus-rtu

Postby vazkus » Wed May 16, 2018 4:02 pm

wow! thank you for taking time and writing such a complete response!

In my implementation I'm using register 0181h to reset the alarm. I actually noticed that it works the first time alarm is triggered, but does nothing to subsequent alarms. Now I know I need to write 0 first clear the alarm reset in order to be able to reset it by writing 1 again. This is not very obvious from documentation (not obvious at all). I will definitely try that.

The second approach of using NET-IN7 is also interesting, I'll give it a try as well. Btw I don't need to save this in non-volatile memory if I do this configuration during the startup, correct?

om_tech_support_AC
Posts: 26
Joined: Tue Jan 03, 2017 2:53 pm

Re: ARD-KD: resetting overvoltage alarm through rs-485/modbus-rtu

Postby om_tech_support_AC » Thu May 17, 2018 7:05 am

Changing NET-IN7 to alarm reset would be a type C timing update. Therefore you would have to write to the non-volatile memory even during start up and would require the cycle of power or executing the configuration command register 397 decimal or 018Dh.