Search found 46 matches

by om_tech_support_AC
Thu Sep 27, 2018 11:28 am
Forum: Stepper Motors and Controls
Topic: Pulse Generator Equivalent to SG61005 (or) PG1200N-D
Replies: 1
Views: 478

Re: Pulse Generator Equivalent to SG61005 (or) PG1200N-D

Hi Sivan, If the SG61005 pulse generator worked with AS98AA-T3.6 then it will work with AR98AA-T3.6-3. For the other pulse generators SG61005 (or) PG1200N-D we not longer offer them in the United States. However you can contact OM India to see if they are still offered or what they suggest for a rep...
by om_tech_support_AC
Tue Sep 18, 2018 6:39 am
Forum: Speed Control Systems
Topic: BMU & BLH Series Clarificatons
Replies: 5
Views: 1538

Re: BMU & BLH Series Clarificatons

Hi Essenceindia, Synchronization is possible for the BLH using parallel operation shown in the linked manual below. If one of the motors needs to run a different speed then a resistor can be wired in between the external voltage or potentiometer. https://www.orientalmotor.com/products/pdfs/opmanuals...
by om_tech_support_AC
Mon Sep 10, 2018 12:11 pm
Forum: General
Topic: AZ series direct input zHome for a while (specific time) and start again automatically
Replies: 5
Views: 2253

Re: AZ series direct input zHome for a while (specific time) and start again automatically

To interrupt the sequence you'll have to use the stop input. For more information about the stop input please refer to the link below. https://www.orientalmotor.com/products/pdfs/opmanuals/HM-60262-6E.pdf#page=101 Then to restart the sequence you can use the Start input only to select operation #0 o...
by om_tech_support_AC
Mon Sep 10, 2018 6:45 am
Forum: Question of the Day
Topic: AZ Series MODBUS Protocal
Replies: 1
Views: 4663

Re: AZ Series MODBUS Protocal

Hi Batum,

I would recommend contacting your local technical support to help walk thru the communication setup with you.

https://www.orientalmotor.com/company/g ... pport.html
by om_tech_support_AC
Thu Sep 06, 2018 7:00 am
Forum: General
Topic: AZ series direct input zHome for a while (specific time) and start again automatically
Replies: 5
Views: 2253

Re: AZ series direct input zHome for a while (specific time) and start again automatically

For setting up the event jump after a torque limit please refer to the forum linked below.

viewtopic.php?f=18&t=11556

Then to restart the process you can link automatic sequential data operation #1 with next data point being #0.

AZ link.JPG
AZ link.JPG (17.29 KiB) Viewed 2171 times
by om_tech_support_AC
Wed Sep 05, 2018 8:06 am
Forum: General
Topic: AZ series direct input zHome for a while (specific time) and start again automatically
Replies: 5
Views: 2253

Re: AZ series direct input zHome for a while (specific time) and start again automatically

Hi Powertek,

What are the part numbers for the AZ motor and driver? Do you want to move to a position then got home wait and then repeat the process?
by om_tech_support_AC
Wed Sep 05, 2018 8:03 am
Forum: Stepper Motors and Controls
Topic: Detection of a revolution with the AZ series
Replies: 3
Views: 615

Re: Detection of a revolution with the AZ series

For the AZM66MK-PS50 which has a 50:1 gear ratio the default steps per one revolution of the output shaft is 50,000. There are two ways to monitor the steps. First is the by reading the pulse output from ASG and BSG which output a signal directly from the ABZO sensor within in the motor. For more in...
by om_tech_support_AC
Wed Sep 05, 2018 7:38 am
Forum: Stepper Motors and Controls
Topic: Microstepping with UDK5128NW2
Replies: 3
Views: 4471

Re: Microstepping with UDK5128NW2

Hi glennsky,

CVD528BR-K can supply 2.8 A/phase and is a New Pentagon type 5 phase driver. CVD528BR-K has a 24 VDC input so depending upon if the Berger Lahr RDM596/50 motor was previously used with a AC input driver it could have reduced torque.
by om_tech_support_AC
Tue Sep 04, 2018 7:03 am
Forum: Stepper Motors and Controls
Topic: Detection of a revolution with the AZ series
Replies: 3
Views: 615

Re: Detection of a revolution with the AZ series

Hi Aro,

What are the part numbers for the AZ motor and driver?
by om_tech_support_AC
Thu Aug 09, 2018 6:53 am
Forum: Linear and Rotary Actuators and Controls
Topic: Communicate with an AZD-KD step driver using a laptop
Replies: 4
Views: 3155

Re: Communicate with an AZD-KD step driver using a laptop

Hi Aro,

With the MWE820A you can convert the RS485 communication or RJ45 connection into a USB connection for a laptop. For more information please refer to the link below.

https://www.orientalmotor.com/products/ ... B_v1_0.pdf
by om_tech_support_AC
Fri Aug 03, 2018 2:03 pm
Forum: General Discussion
Topic: Power Factor of 3IK15A-SW2 induction motor
Replies: 0
Views: 1285

Power Factor of 3IK15A-SW2 induction motor

Q: How do I calculate the Power Factor (output power vs input power ratio) for the motor 3IK15A-SW2? A: For 3IK15A-SW2 first the input power is calculated by multiplying the voltage 220 VAC by current 0.15 A resulting in 33 W. Electric Power.JPG The voltage and current specs for 3IK15A-SW2 can be fo...
by om_tech_support_AC
Thu Aug 02, 2018 8:21 am
Forum: Linear and Rotary Actuators and Controls
Topic: DG200R-ARACD2-1 - Direction
Replies: 3
Views: 4381

Re: DG200R-ARACD2-1 - Direction

Once you wrote 0 to register 0385h you have to save the parameter change to the non-volatile memory. The register for the non-volatile memory is 0191h where you write a 1 to save the change. When you complete the writing to the non-volatile memory cycle the power of the driver.
by om_tech_support_AC
Fri Jul 27, 2018 8:22 am
Forum: Linear and Rotary Actuators and Controls
Topic: DG200R-ARACD2-1 - Direction
Replies: 3
Views: 4381

Re: DG200R-ARACD2-1 - Direction

Hi Jes Peter,

When you changed the Motor Rotation direction did you change it using the MEXE02 software or by writing to register 0385h? When you send a move command over Modbus are you doing absolute movements or incremental?
by om_tech_support_AC
Fri Jul 27, 2018 8:12 am
Forum: Speed Control Systems
Topic: BMU Series Clarifications Required
Replies: 3
Views: 3472

Re: BMU Series Clarifications Required

For the limit switches you could wire them to the FWD and REV external inputs. You could also wire the push button to these external inputs. For the wiring please refer to the linked manual below.
by om_tech_support_AC
Thu Jul 26, 2018 10:49 am
Forum: Speed Control Systems
Topic: BMU Series Clarifications Required
Replies: 3
Views: 3472

Re: BMU Series Clarifications Required

Hi Siva, For your first question do you want the motor to reverse direction when it hits a limit switch? or do you want it to stop? For your second question to stop the motor you'll either need both FWD and REV inputs on for an instantaneous stop or both off for a deceleration stop. For more informa...
by om_tech_support_AC
Wed Jul 25, 2018 6:44 am
Forum: Stepping Motors & Controls
Topic: AR series : query alarm code (modbus)
Replies: 1
Views: 1271

Re: AR series : query alarm code (modbus)

Hi EvanBae,

For the present alarm the upper value will always be 0000 because all the alarms codes can fit in the lower registry. Therefore try reading the lower present alarm register 0081h.
by om_tech_support_AC
Tue Jul 24, 2018 6:57 am
Forum: Stepper Motors and Controls
Topic: ARD-KD closed loop control using external feedback...
Replies: 3
Views: 1317

Re: ARD-KD closed loop control using external feedback...

Yes AZ would allow for speed changes via Modbus to its 256 operations while the motor is operating.
by om_tech_support_AC
Mon Jul 23, 2018 8:16 am
Forum: Stepper Motors and Controls
Topic: ARD-KD closed loop control using external feedback...
Replies: 3
Views: 1317

Re: ARD-KD closed loop control using external feedback...

Hi Vazkus, For the ARD-KD the speed can only be changed between the 64 programmable operations while the motor is running. Once the motor is stopped and the ready output is on then the 64 programmable operations can be changed via Modbus or via our MEXE02 software. Unfortunately there is no way to c...
by om_tech_support_AC
Mon Jul 09, 2018 7:28 am
Forum: Stepper Motors and Controls
Topic: Stepper Motor with Positioning Feedback Signal (like servo motor)
Replies: 9
Views: 2615

Re: Stepper Motor with Positioning Feedback Signal (like servo motor)

Hi Essenceindia, For the external encoder feedback it would be wired to the controller not the CVK drives. If they choose the SCX11 controller linked below are the wiring diagrams for external encoders. https://www.orientalmotor.com/products/pdfs/opmanuals/HM-60080E.pdf#page=71 For the lead wire len...
by om_tech_support_AC
Fri Jun 29, 2018 6:35 am
Forum: Stepper Motors and Controls
Topic: Stepper Motor with Positioning Feedback Signal (like servo motor)
Replies: 9
Views: 2615

Re: Stepper Motor with Positioning Feedback Signal (like servo motor)

Hi essenceindia,

Yes then it would be recommended to use CVK268BK with third party external encoder to get feedback from the motor.
by om_tech_support_AC
Wed Jun 20, 2018 7:13 am
Forum: Stepper Motors and Controls
Topic: Stepper Motor with Positioning Feedback Signal (like servo motor)
Replies: 9
Views: 2615

Re: Stepper Motor with Positioning Feedback Signal (like servo motor)

The CVK series is an open loop system so there is no feedback to the driver. We do offer PKP motors with encoders but the feedback would have to go to a controller. For the controller we offer the SCX11 (linked below) which has an input for an external encoder. https://catalog.orientalmotor.com/item...
by om_tech_support_AC
Wed Jun 20, 2018 7:06 am
Forum: Stepper Motors and Controls
Topic: Looking for a user manual for D2D2043-s
Replies: 1
Views: 396

Re: Looking for a user manual for D2D2043-s

Hi jhchopper,

Below is the manual for D2D2043-S.

D2D2043-S.pdf
(99.53 KiB) Downloaded 26 times
by om_tech_support_AC
Tue Jun 19, 2018 7:12 am
Forum: Stepper Motors and Controls
Topic: Stepper Motor with Positioning Feedback Signal (like servo motor)
Replies: 9
Views: 2615

Re: Stepper Motor with Positioning Feedback Signal (like servo motor)

Hi Essenceindia, For stepper motor and drivers that offer a feedback signal both the AR and AZ series have the ASG/BSG as a feedback output. For the AR series the pulse input type driver offers the resolver feedback via ASG/BSG. For more information about the AR series ASG/BSG output please refer to...
by om_tech_support_AC
Tue Jun 19, 2018 6:54 am
Forum: Speed Control Systems
Topic: BMU & BLH Series Clarificatons
Replies: 5
Views: 1538

Re: BMU & BLH Series Clarificatons

Hi Essenceindia,

For the BMU series there are I/O that can be controlled via a PLC. For information about wiring the I/O please refer to the link below.

http://www.orientalmotor.com/products/p ... df#page=16