Hi,
I have a setup with a ARD-KD driver that runs on 48v power supply. I need to connect 1+ inductive sensors (like Bernstein KIB-M12) for home/limit switching. What is the right way of connecting these sensors? Does the driver provide 24v (or anything <36v) that I can use as a VCC for the sensor?

Thank you.

om_tech_support_KR
Posts: 15
Joined: Thu Jan 11, 2018 3:03 pm

Re: AR-series: home/LS sensors with 48v power supply

Postby om_tech_support_KR » Mon May 14, 2018 12:34 pm

Hi Vazkus,

For the ARD-KD the I/O are open collector type so they do not supply any voltage you will have to supply the 24 VDC externally. We do have a sample wiring for the home/limit sensors when using NPN or PNP type reference them below. They can also be found on page 75 and 76 of the manual I will link it below.

http://www.orientalmotor.com/products/p ... 340-2E.pdf

NPN
npn.png
npn.png (130.42 KiB) Viewed 874 times


PNP
pnp.png
pnp.png (130.69 KiB) Viewed 874 times

vazkus
Posts: 8
Joined: Fri May 11, 2018 2:30 pm

Re: AR-series: home/LS sensors with 48v power supply

Postby vazkus » Mon May 14, 2018 2:29 pm

Thank you very much for your quick and prompt response!

vazkus
Posts: 8
Joined: Fri May 11, 2018 2:30 pm

Re: AR-series: home/LS sensors with 48v power supply

Postby vazkus » Tue Jun 12, 2018 10:57 pm

Dear om_tech_support_KR.

I have a follow-up question regarding homing sensor. I'm trying to use Bernstein KIB-M12NS inductive sensor for HOMES (here's the spec: https://www.bernstein.eu/fileadmin/down ... 6%20xx.pdf), its NPN type sensor and I think I have the wiring set up correctly, it's got a built-in LED that properly indicates the proximity.
I however have trouble interfacing it with the driver. When I measure the voltage between pins 3 and 5 of CN5 I get ~0v in normal condition and jumps to stable 0.7v when it's touching a metal (LED turns on). Am I doing something incorrectly? Do I need a pull-up resistor (the diagram in the pdf file sort of suggests that)?

Thanks!

om_tech_support_KR
Posts: 15
Joined: Thu Jan 11, 2018 3:03 pm

Re: AR-series: home/LS sensors with 48v power supply

Postby om_tech_support_KR » Wed Jun 13, 2018 7:54 am

Hi Vazkus,

How is your sensor wired and to what pins are you wired to on the driver?

vazkus
Posts: 8
Joined: Fri May 11, 2018 2:30 pm

Re: AR-series: home/LS sensors with 48v power supply

Postby vazkus » Sat Jun 16, 2018 12:56 am

Good that you asked this question :)

I checked wiring again and found that it was wrong. IN-COM2 was hooked up to GND, while for NPN sensor type it has to be connected too VCC.